Valve solenoids burning out.
In the past 16 days I have had 4 of 8 solenoids burn out. (Hunter PGV 24vac). I have double checked my wiring and all connections are good and watertight. I want to test the voltage from the Yardian: what is the correct voltage I should expect?
From Hunter’s website:
606800
• Minimum opening/operating voltage: 19 VAC
• Maximum recommended voltage: 28 VAC
• Current at 24 VAC:
• 350 mA inrush, 190 mA holding, 60 Hz
• 370 mA inrush, 210 mA holding, 50 Hz
• Maximum operating pressure: 220 PSI
• Wire leads: 18' of 18 AWG UL-approved wire
-
Official comment
Hi Michael,
Do you have a UK/CA mark on your power adapter product label?
Best Regards,
JosephComment actions -
Hi Michael,
We have been replacing the power adapters since 2023, but for some reason, you still received the older model. We will need to send you a new power adapter, and our support team will assist you at support@aeonmatrix.com.
Best regards,
Joseph -
Got the new power supply last week and installed it (has the UK/CA mark). It’s been rainy most every day here in south Florida so not mush chance for testing.
One day that these system did do a full watering schedule I noticed that the sprinklers in would turn off for a couple of minutes every 10 minutes or so.
No issues with internet and no messages. Only clue was “Yardian Offline”. I have not had a chance to actually check the control unit itself but I think that the power supply may be overheating after a couple of hours running (it takes about 3 hours to do all zones).
I am testing now as I write this and will post anything I observe.