Pump/mechanical valve connection

Comments

4 comments

  • Official comment
    Aeon Matrix

    Hi,

    You will need to use a power relay for your pump. You need to define a zone as a master valve in the Yardian app. You can connect the terminal block of the master zone to the power relay. Please note that the output voltage from the terminal block is 24VAC.

    We have customers using pumps for agriculture application. We will share more information later.

    Best regards,
    Joseph

    Comment actions Permalink
  • Sergio San Jose

    Thanks for the response. So, one cable from the power relay goes to the terminal that would be labeled master valve on the app, and the other cable from the power relay? Do I connect it to the COM terminal or to another zone terminal?

    0
    Comment actions Permalink
  • Aeon Matrix

    Yes, please connect the other wire to the COM terminal.

    0
    Comment actions Permalink
  • Aeon Matrix

    One of our customers uses Yardian for his farm. He connects all terminals to relays because he uses 110V solenoids and 220V pump.

    0