stopping watering task
when I turn on manual, it runs for 2 seconds and turn off again.
-
Official comment
Does this happen everytime on every zone?
Comment actions -
This could be due to the internal current protection mechanism of the Yardian controller. There are two possible causes:
- The load on a single terminal exceeds the maximum current of 1A at 24VAC.
- The inrush current may exceed the limit.
If you haven't connected too many solenoid valves to one terminal, please contact us at support@aeonmatrix.com, and we will provide a command file that can be used with a USB drive to adjust the inrush current protection threshold.
Best Regards,
Joseph -
The valves comes from a rain bird image 6 system.
I try to check the A on valve 1 but couldn’t get it.
Instead I remove the main valve wire and all start as it should now !!!
I don’t understand why ???
Main valve doesn’t work as expected????
I will try without main and let you know !
Thanks for help