  • Official comment
    Aeon Matrix

    Does this happen everytime on every zone?

    Comment actions Permalink
  • Frederic

    yes for each !

     

    0
    Comment actions Permalink
  • Aeon Matrix

    This could be due to the internal current protection mechanism of the Yardian controller. There are two possible causes:

    • The load on a single terminal exceeds the maximum current of 1A at 24VAC.
    • The inrush current may exceed the limit.

    If you haven't connected too many solenoid valves to one terminal, please contact us at support@aeonmatrix.com, and we will provide a command file that can be used with a USB drive to adjust the inrush current protection threshold.

    Best Regards,
    Joseph

    0
    Comment actions Permalink
  • Frederic

    The valves comes from a rain bird image 6 system.
    I try to check the A on valve 1 but couldn’t get it.
    Instead I remove the main valve wire and all start as it should now !!!
    I don’t understand why ???
    Main valve doesn’t work as expected????
    I will try without main and let you know !
    Thanks for help

    0
    Comment actions Permalink
  • Frederic

    A ampère curent consumption

    0
    Comment actions Permalink
  • Aeon Matrix

    Hi Fredederic,

    Do you have a pump relay or a master valve (solenoid valve) in your system?

    What is the main valve wire connected to?

    Joseph

    0
    Comment actions Permalink
  • Frederic

    I thought I have one because it was wired on the old system. But it looks like I don’t ???
    I will ask the man who built the system

    0
    Comment actions Permalink
  • Aeon Matrix

    Hi Frederic,

    If you can run a zone without the main valve wire connected to the M terminal, most likely there's no pump nor a master valve. But it's still better to confirm with the person who built the system. Please keep me posted. Thanks!

    Best Regards,
    Joseph

     

    0
    Comment actions Permalink
  • Frederic

    so he doesn't remember putting a main valve.

    but tonight I try the program (manual) and everything where ok (at least on valves 1 2 and 3)

    I stopped before end (cats where in the garden :P )

    Tonight at 11pm it should start without stopping

     

    thanks for help ;)

    0
    Comment actions Permalink
  • Aeon Matrix

    Hi Frederic,

    Sounds good!
    Please let me know if there's any issue.

    Best Regards,
    Joseph